Hello everyone, I have a general question about sizing transformers. Currently we tell the technicians to figure out the max KVA load then load the transformer to 80% of the predicted max kVA then pick the next highest available transformer.
Now personally i feel we are grossly oversizing these transformers.
If you consider the ANSI Loading Guide (C57.91) it came to a sort of surprise to me that transformers can be loaded to 1.82 times its rated KVA for up to 1 hour. 1.57 x its rated KVA for 2 hours, 1.36 x its rated KVA for 4 hours 1.21 rated KVA for 8 hours. All this without compromising the Normal life span of the transformer.
These values are for a temp of 30 degrees celcius. You add 1.5% additional loading for every degree above 30. I will consider 37 degrees celcius so i will add 12 % additional loading to account for our peak hot climate.
Now this brings into the question our sizing practices. We are rating our transformes at 0.8 of expected peak KVA.
What would you consider a decent rule of thumb for us to rate our transformers. I am thinking that if the load is 110% to 120 % of the rated transformer size then it should work fine.
Example i am thinking if we expect a load of 110 KVA to 120 KVA peak load, then a 100 KVA transformer should be OK???
In your own personal experiences with transformers and how they handle loads what is the rule of thumb that we can go by to choose transformer capacity?????? I think our practice of rating transformers at 80% of peak load is not efficient. What do you use at your utility or what do you think is a good % tage?
Input would be greatly appreciated.
Now personally i feel we are grossly oversizing these transformers.
If you consider the ANSI Loading Guide (C57.91) it came to a sort of surprise to me that transformers can be loaded to 1.82 times its rated KVA for up to 1 hour. 1.57 x its rated KVA for 2 hours, 1.36 x its rated KVA for 4 hours 1.21 rated KVA for 8 hours. All this without compromising the Normal life span of the transformer.
These values are for a temp of 30 degrees celcius. You add 1.5% additional loading for every degree above 30. I will consider 37 degrees celcius so i will add 12 % additional loading to account for our peak hot climate.
Now this brings into the question our sizing practices. We are rating our transformes at 0.8 of expected peak KVA.
What would you consider a decent rule of thumb for us to rate our transformers. I am thinking that if the load is 110% to 120 % of the rated transformer size then it should work fine.
Example i am thinking if we expect a load of 110 KVA to 120 KVA peak load, then a 100 KVA transformer should be OK???
In your own personal experiences with transformers and how they handle loads what is the rule of thumb that we can go by to choose transformer capacity?????? I think our practice of rating transformers at 80% of peak load is not efficient. What do you use at your utility or what do you think is a good % tage?
Input would be greatly appreciated.