Transformer sizing for single phase motor

Status
Not open for further replies.

Alan K

New member
.5 HP pump, 230Volts, Single phase, Full load Amps=8.5, Locked Roter Amps= 30.1A, NEMA Start code "R"

Primary voltage is 480V. What size single phase transformer required for this pump?
 
.5 HP pump, 230Volts, Single phase, Full load Amps=8.5, Locked Roter Amps= 30.1A, NEMA Start code "R"

Primary voltage is 480V. What size single phase transformer required for this pump?
Gross rule of thumb: minimum transformer kVA = 3X the motor HP value if there is nothing else on the circuit and starting across-the-line. So your motor is 1/2HP, use a 1.5kVA transformer minimum.
 
130525-0906 EDT

Alan K:

0.5 HP 230 V and full load = 8.5 A looks wrong. VA = 1955. 0.5 HP output = 746/2 = 373 W. If you assume 85% efficiency and 0.8 PF, then VA = 550. A 1/2 Hp Sears motor of mine at 230 is labeled 4.3 A, or 989 VA. Are you reading the the 115 V full load amperes?

.
 