Transformer Sizing Help

Status
Not open for further replies.

lazercrazy3

Member
Location
Chicago
Occupation
Electrical Engineer
I am trying to size a drive isolation transformer for the purpose of eliminating harmonics to chiller equipment. Right now I have a 480V 3-phase panel that is powering a 460V 3-phase chiller. Should I size the transformer for 480-460 or 480-480? I keep getting mixed answers from others. Thanks.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
The 460V rating is what is normally seen on equipment intended for 480V distribution, to allow a bit of voltage drop. In other words a motor nominally rated at 460V is expected to be connected to a supply nominally rated at 480V

So size 480-480 unless you have a specific (and unlikely) instruction otherwise from the equipment manufacturer.

-Jon
 

lazercrazy3

Member
Location
Chicago
Occupation
Electrical Engineer
The 460V rating is what is normally seen on equipment intended for 480V distribution, to allow a bit of voltage drop. In other words a motor nominally rated at 460V is expected to be connected to a supply nominally rated at 480V

So size 480-480 unless you have a specific (and unlikely) instruction otherwise from the equipment manufacturer.

-Jon
Thanks Jon.
 