It is my understanding that a transformer must be sized to meet the calculated load which it serves. For instance if a load is calculated to be 900kVA a 1000kVA transformer must be used and a lower sized transformer cant be used even if it is known that the load will never reach the calculated load? In other words the transformer rating must meet or exceed the calculated load?
Does this mean that the transformer base rating must be greater than calculated load or can one of the forced air ratings of a transformer be used to exceed the load even if base rating doesn't?
The only time I believe where a transformer doesn't need to meet or exceed calculated load is a utility owned transformer since they do not need to adhere to NEC?
Does this mean that the transformer base rating must be greater than calculated load or can one of the forced air ratings of a transformer be used to exceed the load even if base rating doesn't?
The only time I believe where a transformer doesn't need to meet or exceed calculated load is a utility owned transformer since they do not need to adhere to NEC?