We have a transformer rated at 600amp on the secondary. Downstream is a breaker set at 900amp trip. Is it correct to say the transformer size needs to be sized for duty load only and not full load of the facility?
We have a transformer rated at 600amp on the secondary. Downstream is a breaker set at 900amp trip. Is it correct to say the transformer size needs to be sized for duty load only and not full load of the facility?
There is insufficient information in your question to give you an answer, including what you mean by "duty load".
The vulture's are circling. :lol:
We have a transformer rated at 600amp on the secondary. Downstream is a breaker set at 900amp trip. Is it correct to say the transformer size needs to be sized for duty load only and not full load of the facility?
Generally a transformer must be sized for the loads it will see - oversized to handle any internittent loads such as motor starting.
Transformers do not need to be over-sized, per se, it must be capable of providing the Watts and VARS to the electrical system it serves during starting of loads (which includes motors), such that the voltage drop on the system remains within acceptable limits. Selection of proper impedance is necessary. Simply over-sizing is not necessarily the answer.
where does it say this in the code?
But I have those sizing rules right here in my shirt pocket somewhere.....It won't because as we all know the NEC is not intended as an engineering design guide, it is minimum requirements to provide safety.
I believe 90.1 makes that quite clear.
90.1(C) does not say the NEC is not part of the design process, it says that the NEC is not sufficient to be the only reference used.But I have those sizing rules right here in my shirt pocket somewhere.....
where is this in the code?
does not say anything at all about xfmr size. only about conductors.Don't know - never looked for it in the code. I never expected a document that starts out saying:
90.1 Purpose.
(B) Adequacy. This Code contains provisions that are considered
necessary for safety. Compliance therewith and
proper maintenance results in an installation that is essentially
free from hazard but not necessarily efficient, convenient,
or adequate for good service or future expansion of
electrical use.
and followed by:
(C) Intention. This Code is not intended as a design specification
or an instruction manual for untrained persons.
to address the need for an electrical system to actually work. Although, my continued employment likely requires that the systems I work on - work reliably. I know that just seems mean as can be on their (my customers) part, but that's the way they are.
Maybe look at 210.11, then go to 215 for the feeders.
Did you have something else in mind?
ice
90.1(C) does not say the NEC is not part of the design process, it says that the NEC is not sufficient to be the only reference used.
Jimbo, where does it say that? :? My 90.1(C) reads; "This Code is not intended as a design specification or an instruction manual for untrained persons".
Further, 90.1(B); Adequacy. This Code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance results in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.
Could you elaborate on where your wording is found? :roll:
...part of the design process is to ensure that the system actually works while incorporating the requirements in the code that are mostly oriented toward reducing hazards from the use of electricity.
does not say anything at all about xfmr size. only about conductors.
... i am a little suspicious of the statement that the xfmr is rated 600A secondary. I know of no transformers that are rated that way.
Could you elaborate on where your wording is found?