What size transformer do i need to feed a panel. Primary 400 amp 277/480 to 120/ 240 200 amp all three phase.
+1.240 volts, 3 phase @ 200 amps is 83 kva.
The closest standard size would be 75 kva and that wold normally be sufficient but there are so many pitfalls it approaching it from this angle anything is possible.
As already mentioned, Step 1 is to determine to load. In your case, load per phase would be important as neutral loading could be pertinent.