Transformer sizing

Status
Not open for further replies.

dronai

Member
Location
Ca.
I have to size a transformer 480V/240V for a 35A 240V 3-P Chiller. The load is about 14KVA, is a 15KVA too small, or should I put in a 20 KVA ?
 
This would depend on whether you want to leave room for expansion. I believe a transformer is rated at 100% so you can get by with the 15kva unit
 
I have to size a transformer 480V/240V for a 35A 240V 3-P Chiller. The load is about 14KVA, is a 15KVA too small, or should I put in a 20 KVA ?

Your going from 480V 3-ph to 240V high leg delta? Odd Choice, but ok....

What kind of chiller? They should have a cut sheet that says minimum circuit amps and MOCP along with other characteristics, e.g. starting info.

Most likely you will need at least a 30KVA. There is no such thing as a 20KVA standard size anyway.
 