tarun
Member
- Location
- North Carolina
I have three machines: 230/1/60 and rated 48.5A each. I have to feed these three machines using a 3-phase panel (thru 2 pole breakers)
Machine#1: fed from Phase A&B
Machine#2: fed from Phase B&C
Machine#3: fed from Phase A&C
I need to put a 3-phase, 480/240V transformer before this panel. I am confused if I need a 30 KVA transformer or a 45 KVA transformer.:angel::angel:
Calculation 1: Each machine needs 48.5 x 240 = 11640 VA
So, total 3 x 11640 = 34920 VA
Hence I need atleast 35KVA transformer, next available size will be 45KVA
Calculation 2: Full load secondary current of 30KVA transformer is 72.2A. I have a 100% balanced load on three phases, so basically I have 48.5A required at each phase. Then 30 KVA trnasformer should be enough.
Machine#1: fed from Phase A&B
Machine#2: fed from Phase B&C
Machine#3: fed from Phase A&C
I need to put a 3-phase, 480/240V transformer before this panel. I am confused if I need a 30 KVA transformer or a 45 KVA transformer.:angel::angel:
Calculation 1: Each machine needs 48.5 x 240 = 11640 VA
So, total 3 x 11640 = 34920 VA
Hence I need atleast 35KVA transformer, next available size will be 45KVA
Calculation 2: Full load secondary current of 30KVA transformer is 72.2A. I have a 100% balanced load on three phases, so basically I have 48.5A required at each phase. Then 30 KVA trnasformer should be enough.