southman
- jacksonville, fl
I have 16 temp office trailers coming in. They each have two (2) 125 amp panels with 120/240 single phase service. What size 3-phase transformer should I spec out?
Do you mean 120/208V single phase service to each trailer instead of 120/240V?
The trailer spec provided has "120/240 single phase", but you're right it has to be 120/208. The HVAC is 6.0 ton unit with 20kw heat strip.
Load calc! We don’t need no stinkin’ load calc!
Just total it all up. It only comes out to ~1.5 MW. :blink:
No problem.
Demand factors and all that stuff is too much trouble.
ac 10 kva per trailer
ht 20 kva
in FL chances are all AC will run at the same time 100% demand 160 kva
figure 75% for htg 225 kva
10 kva max ltg/recept per trailer 160 kva
350 kva sounds close
But 300 kVA is a standard size.
I am gonna need you to be a little more “creative”.
run it hot and hope for the best
Typically the POCO will size the number and size of the trannies.
Depending on how spread out the trailers are, I'm guessing they will just put in 3 separate 120/240 1 phase, 25 kVA and call it good unless you fry one of them soon.