Transformer sizing.

Status
Not open for further replies.

ElectricMatt

Senior Member
Location
Waco, tx
I am looking for some opinions here. I am working off of the knowledge I have and want to make sure there is something I am not missing before bringing up this discussion to the my engineer.

I am putting in a boiler room, the transformer for the low voltage panel is a 75kva 480v to 208v, 98.6 eff @35% loading. It feeds a 60 circuit panel with a 250a main.

By my calculations a 75kva transformer is only good for 208a. Obviously the connected load as engineered is well below 250amps, however is it legal to size the main breaker so high over the transformers capacity? Please enlighten me and explain why this is/is not acceptable.

Thank you!


Sent from my iPhone using Tapatalk
 

ElectricMatt

Senior Member
Location
Waco, tx
3d6b8b3697be5437495c75d3f39fed56.jpg


I attached a picture of the panel schedule with load calculations


Sent from my iPhone using Tapatalk
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
125% of 208A is 260A. Sizing it 250A is actually being conservative based on the Panel rating. The Main Bus/Panel is rated 250A, but the Main Breaker is supposed to be 225A. Not sure where you are getting the main to be 250A?
 

ElectricMatt

Senior Member
Location
Waco, tx
125% of 208A is 260A. Sizing it 250A is actually being conservative based on the Panel rating. The Main Bus/Panel is rated 250A, but the Main Breaker is supposed to be 225A. Not sure where you are getting the main to be 250A?

I am getting he 250amp main breaker from my one line diagram.


Sent from my iPhone using Tapatalk
 

ElectricMatt

Senior Member
Location
Waco, tx
125% of 208A is 260A. Sizing it 250A is actually being conservative based on the Panel rating. The Main Bus/Panel is rated 250A, but the Main Breaker is supposed to be 225A. Not sure where you are getting the main to be 250A?

So on the secondary side of a transformer you are allowed to add 125% or the rated full load of the transformer?


Sent from my iPhone using Tapatalk
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
So on the secondary side of a transformer you are allowed to add 125% or the rated full load of the transformer?


Sent from my iPhone using Tapatalk

With a 125A primary circuit breaker, the secondary circuit breaker can be any size, per T450.3(B) "Primary only protection." 250A seems reasonable.
 

ElectricMatt

Senior Member
Location
Waco, tx
With a 125A primary circuit breaker, the secondary circuit breaker can be any size, per T450.3(B) "Primary only protection." 250A seems reasonable.

I don’t have my code book with me right now, but to make sure I am understanding this .

480 v primary 75kva = 90.3 fla

90.3 x1.25 =112.9 amps

Next size breaker up is allowed which would be 125a.

Is this correct?


Sent from my iPhone using Tapatalk
 

ElectricMatt

Senior Member
Location
Waco, tx
I am not questioning anyone, I have not done many transformer calculations so I want to make sure I understand the necessary calculations and the theory behind them.

Thank you for he responses so far very helpful!


Sent from my iPhone using Tapatalk
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I don’t have my code book with me right now, but to make sure I am understanding this .

480 v primary 75kva = 90.3 fla

90.3 x1.25 =112.9 amps

Next size breaker up is allowed which would be 125a.

Is this correct?


Sent from my iPhone using Tapatalk
That is correct. If the primary OCPD was larger than 125A then the secondary OCPD would be limited to 300A maximum.
 

JFletcher

Senior Member
Location
Williamsburg, VA
I don’t have my code book with me right now, but to make sure I am understanding this .

480 v primary 75kva = 90.3 fla

90.3 x1.25 =112.9 amps

Next size breaker up is allowed which would be 125a.

Is this correct?


Sent from my iPhone using Tapatalk

Yes, that is correct. Matter of fact because your primary protection is sized at 125% or less, the secondary protection is not even required. That it is 225 or 250 amps is irrelevant.

edited to add... I see on the diagram that the panel main circuit breaker is 225 amps and that the mains rating is 250 amps. What you have described thus far is a perfectly compliant code installation.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
With a 125A primary circuit breaker, the secondary circuit breaker can be any size, per T450.3(B) "Primary only protection." 250A seems reasonable.

I don't think that "Not Required" is the exactly the same as "can be any size"; understanding in the context you are talking about the transformer only but your statement could be misleading when it comes to the panelboard which in this case would be limited to 250A, maximum.
 