If I have a 750kVA transformer 13.8:208Y/120V, the secondary OCP would be 3000A.
750/0.36*1.25 = 2600 -> next size up = 3000A.
However, if I don't need the full 750kVA could I downsize the OCP?
3000A is the maximum OCP, but theoretically could I put a secondary OCP of 2500A or even 2000A - knowing 2000A is more than I need?
Reason: the transformer is a spare transformer that the owner has on site, they want to use it for a temporary application to feed temporary distribution equipment, they would be renting the secondary OCP, and my thought is that 3000A frame is significantly more rare than a 2000A frame, so renting a 2000A frame would be both more cost effective and will have shorter lead times.
Thoughts?
750/0.36*1.25 = 2600 -> next size up = 3000A.
However, if I don't need the full 750kVA could I downsize the OCP?
3000A is the maximum OCP, but theoretically could I put a secondary OCP of 2500A or even 2000A - knowing 2000A is more than I need?
Reason: the transformer is a spare transformer that the owner has on site, they want to use it for a temporary application to feed temporary distribution equipment, they would be renting the secondary OCP, and my thought is that 3000A frame is significantly more rare than a 2000A frame, so renting a 2000A frame would be both more cost effective and will have shorter lead times.