Transformer Sizing

Status
Not open for further replies.

3hots

New member
Here`s my situation, I have 15 heating circuits (3 phase) ,11 - 240 volt with a total of 210 amps max draw, 4 120 volt circuits witha max draw of 40 amps. 210 + 40=250 amps total. What TF do I need 112.5 kva or can I get by with a 100 kva, No motors, just heating elements.
 
That would appear to require a 3 phase 4 wire wild leg delta transformer. As I recall you are very limited as the the amount of single phase 120 volt load you can place on these transformers. I think that this only applies to three phase delta/delta transformers.
Don
 
heating loads

heating loads

Don is correct. You state that the heating loads are 240V and 120V so I assume you are using a Mid-Tap transformer. Here is the note GE shows under the application of a Mid-Tap transformer and I have found other manufactures to have the same stated limitations. " When utilizing the 120V midtap for single-phase applications, the single-phase load should not exceed 5 percent of the three-phase kva rating. The three-phase kva load must be redduced by the same percentage as that added by the single-phase load. Additional loading beyond the 5% may cause the transformer to over heat and fail. If single-phase load is in excess of 5%, it is recommended that a separate single-phase unit be used to handle the load". Something to consider as long as your loading falls withing the 5% and the three-phase loading falls within its adjustment you should be ok. On your 112.5kva you would have about 107kva of three-phase if you used the full 5% on single-phase of 5.625kva.
 
You could consider using a 208Y/120 transformer. The effective power would be reduced, but you should be able to get by with a 75kVA, especially if you can derate based on total percentage on time.
 
Status
Not open for further replies.
Top