REEngineer
Member
There is a load list summary report for this plant and based on it, I'm going to size substation transformer. But why so many terms in the report.
Plant has three kind of loads: Normal, Essential, Vital. All loads can be categorized into Continuous, Intermittent and standby. For every load we have two power data, Mechanical(The shaft power) and Rated(Installed power).
Cyclic Factor, Power Factor, Efficiency and Load Factor for each load is determined (or predetermined).
My procedure was like this:
1) Absorbed Power = (Mechanical Power/Efficiency) * Cyclic factor.
2) Absorbed KVAR = Absorbed Power * TAN(ACOS(Power Factor)).
3) Capacity = Sum(Absorbed KVAR) * 1.15
And the next recommended value in IEC37 was chosen for each transformer.
These are the questions:
1) Should I try to size transformers based on Rated power instead of Absorbed power? This way, larger sizes would be estimated.
2) If calculation shows 200KVA transformer is needed for one bus bar and 400KVA transformer for the other, isn't it better to select both as 400KVA? Of course the two mentioned bus bars are not going to be paralleled. I just have this feeling that it's better to have exactly same transformers in one substation for a specific voltage rating and it may be better for maintenance.
Plant has three kind of loads: Normal, Essential, Vital. All loads can be categorized into Continuous, Intermittent and standby. For every load we have two power data, Mechanical(The shaft power) and Rated(Installed power).
Cyclic Factor, Power Factor, Efficiency and Load Factor for each load is determined (or predetermined).
My procedure was like this:
1) Absorbed Power = (Mechanical Power/Efficiency) * Cyclic factor.
2) Absorbed KVAR = Absorbed Power * TAN(ACOS(Power Factor)).
3) Capacity = Sum(Absorbed KVAR) * 1.15
And the next recommended value in IEC37 was chosen for each transformer.
These are the questions:
1) Should I try to size transformers based on Rated power instead of Absorbed power? This way, larger sizes would be estimated.
2) If calculation shows 200KVA transformer is needed for one bus bar and 400KVA transformer for the other, isn't it better to select both as 400KVA? Of course the two mentioned bus bars are not going to be paralleled. I just have this feeling that it's better to have exactly same transformers in one substation for a specific voltage rating and it may be better for maintenance.