I have an existing building with 100 A 480V service. Drawing calls for 225A 120/208V panel w/ connected load= 58.3KVA, demand load= 44.69KVA.
There is also a 16.5KW RTU on the existing 480V panel.
1. Do I size the transformer based on demand or actual total load?
2. Assuming it is based on demand, I calculated 124A on secondary44690/208/1.732, 54A on primary 44690/480/1.732
3. Based on connected load, 162A secondary 58300/208/1.732, 70A primary 58300/480/1.732.
4. I then add the RTU load 16500/480/1.732=19.85A
5. If I calculated correctly the existing 100A 480V service is adaquate.
6. My next question is what size transformer do I need. 45, 50, 60 KW?