Greetings!
I've been delving into the NEC and trying to increase my understanding of power here recently. Hopefully in the future, I will be able to answer your questions! So let me start:
I have a delta-to-wye transformer rated @ 20kVA. It is converting 115VAC, Delta (3PH) to 200/115VAC, Wye (3PH), and is to deliver a total of 80A (continuous). From my calculations I get the following:
I = apparent power/Voltage (line-to-line) = 20kVA/200 = 100A
since 3PH: 100A/sqrt(3) = 57.7A
Questions: Will a 20kVA xfrmr be enough to deliver a max load of 80A?
Is the 57.7A the total amperage delivered per phase/line or is it the total of all three phases? In other words, is each phase delivering 19.3A (57.7A/3)???? (or perhaps the 100A is the total and it's 57.7A per phase).
Thanks in advance for your help! Of course, let me know if you require more information/clarification.
I've been delving into the NEC and trying to increase my understanding of power here recently. Hopefully in the future, I will be able to answer your questions! So let me start:
I have a delta-to-wye transformer rated @ 20kVA. It is converting 115VAC, Delta (3PH) to 200/115VAC, Wye (3PH), and is to deliver a total of 80A (continuous). From my calculations I get the following:
I = apparent power/Voltage (line-to-line) = 20kVA/200 = 100A
since 3PH: 100A/sqrt(3) = 57.7A
Questions: Will a 20kVA xfrmr be enough to deliver a max load of 80A?
Is the 57.7A the total amperage delivered per phase/line or is it the total of all three phases? In other words, is each phase delivering 19.3A (57.7A/3)???? (or perhaps the 100A is the total and it's 57.7A per phase).
Thanks in advance for your help! Of course, let me know if you require more information/clarification.