Transformer System Bonding Jumper - Factory Strap

Status
Not open for further replies.

ron

Senior Member
Trying to find in the code where I am allowed to use the factory supplied transformer system bonding jumper bus of unknown size, rather than have to replace it with a known 250.102(C)(1) wire type.
I know that 250.28(A) allows a wire OR bus, but I have no way to easily convert the bus provided from the manufacturer size to the wire size in the table.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It may not be the case in youe situation but many transformers come with a "strap" that I believe simply bonds the core and is often mistaken for a bonding strap. If there is any question, you might check continuity to assure the strap you describe is actually connected to "XO"
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It may not be the case in youe situation but many transformers come with a "strap" that I believe simply bonds the core and is often mistaken for a bonding strap. If there is any question, you might check continuity to assure the strap you describe is actually connected to "XO"
I agree, as I have never seen a transformer that had a factory installed system bonding jumper.
 

ron

Senior Member
I haven't either on a dry transformer. But maybe Ron is referring to utility style oil filled units that often have one.
It is a 3MVA transformer and it is far from me, so I do not have a picture handy, but I'm being asked if it has to be replaced with a wire type by guys in the field. I will have them check continuity, just in case.
Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I haven't either on a dry transformer. But maybe Ron is referring to utility style oil filled units that often have one.
Unlike the dry transformers I was referencing, I have seen 3MVA transformers with a neutral bond strap and always accepted them it as being correctly sized by the manufacturer.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Are you aware of a code section like 408.3(C) that would allow it formally?
Not really. If it's factory supplied I would say 90.7 which precludes factory installed internal wiring of equipment in the same manner we don't question factory main bonding jumpers supplied with switchboards.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
This thread has me really curious and I expected it to have about 30-40 replies already.
Sort if interested in the pros opinion on this also..
I did find this.. It’s a little old, but…

 