I would like to install a 75KVA, 480V to 208Y/120V transformer with primary only protection of 125A. On the secondary, I would like to use a 350KCM tap (rated at 310A, and less than 25' long) to feed two 150A circuit breakers (or maybe fused switches). Each circuit breaker would then feed a 1/0 wire to a 200A panel.
Do you all think this allowed by 240.21(C)(3)?
The reason I want to do this is so I can protect the secondary at more than 200A (so I can get the whole 75KVA without worrying about tripping a breaker or blowing fuse), but I don't want to run 4/0 or larger to both panels (each more than 25' away).
Steve
Do you all think this allowed by 240.21(C)(3)?
The reason I want to do this is so I can protect the secondary at more than 200A (so I can get the whole 75KVA without worrying about tripping a breaker or blowing fuse), but I don't want to run 4/0 or larger to both panels (each more than 25' away).
Steve