charlie
Senior Member
- Location
- Indianapolis
I received the following e-mail and thought you would be interested in the content.
I am interested in 240.21(C)(2) Transformer Secondary. Paragraph (1)(b) requires that the rating of the conductors be not less that the rating of the OC device. An example is a 400 ampere breaker in 400 ampere panel. Following (1)(b) the conductor should be 600 kcmil. However I think the CMP meant to allow 500 kcmil at 380 amps. Many inspectors enforce the 600 kcmil and do not allow the next size breaker as stated in 240.4(B). Will you see if this is being clarified?
I am interested in 240.21(C)(2) Transformer Secondary. Paragraph (1)(b) requires that the rating of the conductors be not less that the rating of the OC device. An example is a 400 ampere breaker in 400 ampere panel. Following (1)(b) the conductor should be 600 kcmil. However I think the CMP meant to allow 500 kcmil at 380 amps. Many inspectors enforce the 600 kcmil and do not allow the next size breaker as stated in 240.4(B). Will you see if this is being clarified?