Yesterday I posted about my coworker who wanted to feed a single phase panel’s A phase from a 30KVA 480 volt delta primary / 208Y-120 volt secondary output x1 terminal, then panels neutral fed from transformers x2 and finally panels B phase from the transformers secondary output x3 terminal
This was obviously wrong. He finally listened to me and replaced the single phase panel with a 3 phase panel.
However, the fixed machine he was trying to power up required 3 phase 240 volts but output on standard transformer taps provided around 208 volts phase to phase as expected and the machine would not run
My question is that while my coworker did not want to change the transformer to a 480/240 volt separately derived system and although I knew I could boost the output voltage by changing the taps to the max output setting (as if the incoming voltage was lower than nominal), the input voltage was on the high end 509 volts due to utility substation.
Although I did not like using this method I was able to get output voltage to the target 240/120 volts out from this 30KVA 480 delta/ 208Y-120 transformer
My concern is that as shown in the transformer label, this max tap setting is available if incoming voltage was on the low side 432 volts. Therefore, would doing this as a cheap way to boost voltage harm the transformer which were meant to see a lower primary voltage under this tap setting?
This was obviously wrong. He finally listened to me and replaced the single phase panel with a 3 phase panel.
However, the fixed machine he was trying to power up required 3 phase 240 volts but output on standard transformer taps provided around 208 volts phase to phase as expected and the machine would not run
My question is that while my coworker did not want to change the transformer to a 480/240 volt separately derived system and although I knew I could boost the output voltage by changing the taps to the max output setting (as if the incoming voltage was lower than nominal), the input voltage was on the high end 509 volts due to utility substation.
Although I did not like using this method I was able to get output voltage to the target 240/120 volts out from this 30KVA 480 delta/ 208Y-120 transformer
My concern is that as shown in the transformer label, this max tap setting is available if incoming voltage was on the low side 432 volts. Therefore, would doing this as a cheap way to boost voltage harm the transformer which were meant to see a lower primary voltage under this tap setting?