3. Reverse feeding
Step-down transformers are occasionally used as a step-up transformer by “reverse feeding” or “back feeding” the transformer.
Reverse feeding is simply a matter of having the power supply enter at the low voltage windings.
Given the greater availability of step-down transformers, reverse feeding is a fairly common practice. With that said, there are some important things you should consider before making the decision to reverse feed.
There are four main issues with reverse feeding:
Code compliance
NEC 450.11 (B) permits a transformer to be fed from the secondary side of the transformer as long as the installation complies with the manufacturer's instructions. The code reads as follows: "A transformer shall be permitted to be supplied at the marked secondary voltage, provided that the installation is in accordance with the manufacturer's instructions."
This is typically the reference that is cited for reverse feeding transformers by inspectors to ensure an installation complies.
So while there’s nothing in the NEC that directly prohibits reverse-feeding, your local electrical inspector may decide they want to see language on the transformer nameplate like “suitable for step-up operation” or “rated for bi-directional use” before approving the installation.
Voltage Taps
Transformer voltage taps are included by default on the primary windings. When you reverse feed a step-down transformer, you lose the ability to adjust the primary voltage rating to accommodate for small discrepancies in the supply voltage. And if there is more than a 5% variance, the windings will over-excite causing excess heat and energy loss. This can result in either saturation of the windings, or a failure to produce secondary voltage.
Inrush
Inrush current (the amount of current the transformer draws when initially energized) can be up to 16 times greater when reverse-feeding, which could result in nuisance tripping of fuses and circuit breakers.
This greater inrush occurs because normally the output winding is wound first and is therefore closest to the
transformer core. When a transformer is back-fed, the inner winding is energized first.
Sizing a larger breaker for the excess load may violate code. The greater the kVA the greater the inrush, which is why some manufacturers recommend you only reverse feed transformers 75 kVA and below.
Vector grouping / No neutral
The most common transformer vector group is DELTA-WYE, with DELTA being the configuration on the primary side, and WYE on the secondary side. Therefore, reverse feeding a transformer originally designed for step-down operation will result in a DELTA secondary connection, which lacks a neutral.