transformer taps

Status
Not open for further replies.

fuzzbutt

Member
How do you set the taps on a 480 volt transformer and to what voltage? is it 512 volt at full load or is it 480 plus 10% at full load? what is the proper procedure?
 
Re: transformer taps

this a 3 phase transformer and according to the Ramsay test they say there is a procedure for setting the taps. i have looked and asked around and I can't find a thing/
 
Re: transformer taps

I'm not familiar with Ramsay Test.
Set the primary tap so that you get the voltage on the secondary you want. As you load the secondary, the secondary voltage will drop in proportion to the listed impedance of transformer.
Half load with a 5% transformer, drops the secondary voltage 2.5%
 
Re: transformer taps

In our area the utilities offer (depending on the jurisdiction of the project) 480/277 or 460/265, it is up to the contractor to determine the nominal voltage and set taps accordingly. In the past we have had projects with low voltage due to a variety of problems the utility would not or could not address, we monitored the secondary voltage for a extended period of time and adjusted taps to accommodate the low primary voltage.
We rechecked the voltage periodically as voltage levels can change based upon time of year and loads on the distribution system.

[ May 31, 2005, 07:52 AM: Message edited by: brian john ]
 
Re: transformer taps

Measure the supply voltage to the primary. Set the primary taps to the measured voltage. Set the secondary taps to the desired nominal voltage. Check the output voltage after making the connections. Measure the primary and secondary voltage under load.
 