Re: transformer taps
In our area the utilities offer (depending on the jurisdiction of the project) 480/277 or 460/265, it is up to the contractor to determine the nominal voltage and set taps accordingly. In the past we have had projects with low voltage due to a variety of problems the utility would not or could not address, we monitored the secondary voltage for a extended period of time and adjusted taps to accommodate the low primary voltage.
We rechecked the voltage periodically as voltage levels can change based upon time of year and loads on the distribution system.