Hi all, I am not a transformer guy, so admittedly in over my head but I want to get this right for the customers sake. The customer has an old 3ph 30kva 208Y to 480D transformer next to the main service. We replaced the main service and installed a breaker panel that we then tied the transfer to on a 3 pole 100A breaker. Originally the #4 bond wire from the ground rods was tied to the XO on the transformer. When we replaced the service, we added a #4 in our conduit and bonded it in the breaker panel. I just read an old thread on here detailing why that is a bad idea, as the unbalanced load from the 480 side goes back onto the XO. They are having bad voltage on the load side and when I got there, the ground wire was melted between the XO and the breaker panel. So I know I need to remove the bond from the XO and only install it on the frame of the transformer. Why is/did the bond wire going to the ground rods not have any issues?
OK, now for the real question. The other side is going to another 37.kva 208y to 480 delta transformer that then drops the voltage back down to 208 and that feeds a breaker panel for a small house. They did this to limit the voltage drop as the distance between the two transformer is significant. Running between the transformers is just 3 conductors. How should the transformer at the other end be bonded?
Here is is in short hand:
100amp three pole breaker feeding 208v going 10ft to 208y480d transformer from there it is 3 wires from going 700ft to 800ft to a small house to another 208y / 480d transformer then 20 feet to a breaker panel.
The old label is the transformer at the service, and the FPT is the transformer at the house (load side)
Can you confirm what the bonding should look like at both transformers so this is electrically safe and performs correctly.
This is a camp so lots of people coming and going who stay in the house this is serving.
Thanks for your help!
OK, now for the real question. The other side is going to another 37.kva 208y to 480 delta transformer that then drops the voltage back down to 208 and that feeds a breaker panel for a small house. They did this to limit the voltage drop as the distance between the two transformer is significant. Running between the transformers is just 3 conductors. How should the transformer at the other end be bonded?
Here is is in short hand:
100amp three pole breaker feeding 208v going 10ft to 208y480d transformer from there it is 3 wires from going 700ft to 800ft to a small house to another 208y / 480d transformer then 20 feet to a breaker panel.
The old label is the transformer at the service, and the FPT is the transformer at the house (load side)
Can you confirm what the bonding should look like at both transformers so this is electrically safe and performs correctly.
This is a camp so lots of people coming and going who stay in the house this is serving.
Thanks for your help!