Hi all,
I would like to seek an assistance about an concern on removing all FDAS at transformer vault room initiated by electric power distributor. But for the compliance electronic code, still theres a need for FDAS. So i would like to clarify for NEC if installing an heat detectors inside the exhaust duct of transformer vault room. Is there a code violation on NEC or, any concern maybe as for your experiences specially on life safety matters. Thank you. Hoping for your kind reply.
 
HI whats a FDAS? It says your in Asia, is the NEC being applied to a project in Asia?

The requirements for transformer vault rooms can be found in part III of NEC article 450, section 450.45 deals with ventilation openings.
Its a pretty short read.
Depending on where you project is there are other codes that impact this so its important to know where the project is.
 
HI whats a FDAS? It says your in Asia, is the NEC being applied to a project in Asia?

The requirements for transformer vault rooms can be found in part III of NEC article 450, section 450.45 deals with ventilation openings.
Its a pretty short read.
Depending on where you project is there are other codes that impact this so its important to know where the project is.
I’m thinking fire department alarm system
 