Based on this topic:
http://forums.mikeholt.com/showthread.php?t=182554&p=1812493#post1812493
Could one have a 120/240/480V system, using a center tapped 240V xfmr for the 120/240, and have 480V on the other 2 phases? Or even a double 'neutral' tapped 1ph 480xfmr; instead of a midpoint neutral tap, taps at 1/4 and 3/4 of the windings? You could have 480V delta with 120V from A to "neutral 1", 240V between N1 and "neutral 2" (or 240V from A to a center tap), and 120V between N2 and B. With 480V 3ph between AB, BC, and AC. If one needed just 480V single phase, but also 120V and 240V, could that be achieved with one transformer wired in a manner described above?
http://forums.mikeholt.com/showthread.php?t=182554&p=1812493#post1812493
Could one have a 120/240/480V system, using a center tapped 240V xfmr for the 120/240, and have 480V on the other 2 phases? Or even a double 'neutral' tapped 1ph 480xfmr; instead of a midpoint neutral tap, taps at 1/4 and 3/4 of the windings? You could have 480V delta with 120V from A to "neutral 1", 240V between N1 and "neutral 2" (or 240V from A to a center tap), and 120V between N2 and B. With 480V 3ph between AB, BC, and AC. If one needed just 480V single phase, but also 120V and 240V, could that be achieved with one transformer wired in a manner described above?