Transformer voltage

Status
Not open for further replies.

Ainsley Whyte

Senior Member
Location
Jamaica
Occupation
Senior Electrical Engineer
TR-3 XMFR
SEC. FEEDER
2.4/4.16KV SWG

I have seen this on a electrical distribution system and trying to understand the voltage

I know it is the secondary voltage of the transformer switch gear . but 2.4/4.16KV ( WHAT IS IT SAYING CAN SOMEONE EXPLAIN ?)
 
SO for a TR-4 XMFR
SEC. FEEDER
1.387/2.4KV SWG is a Wye secondary that will be 2400V line to line and 1387V line to neutral.

this should be correct ??
 
Last edited:
no we actually have 2400v voltage line to line
2400 volts line to line was a common industrial voltage system around here a long time ago. It was almost always an ungrounded delta system. I worked on a couple of projects where we changed the distribution voltage from 2400 to 4160. The transformer banks were all made up 3 single phase transformers, so we just changed the primary connections from delta to wye when the supply voltage was increased.
 
2400 volts line to line was a common industrial voltage system around here a long time ago. It was almost always an ungrounded delta system. I worked on a couple of projects where we changed the distribution voltage from 2400 to 4160. The transformer banks were all made up 3 single phase transformers, so we just changed the primary connections from delta to wye when the supply voltage was increased.
What was the advantage to change from 2400 to 4160 v
 