Transformer vs door opening distance

Status
Not open for further replies.

bryanrj1

New member
Location
Illinois
This is a code question. We have a wall mounted 480 volt 10 kva transformer mounted right next to a door opening such that when the door is opened the door hits the transformer. The door is for people to pass through. Is there a code violation here? Is there a code requirement that states a minimum distance between the transformer and the door opening?
 
This is a code question. We have a wall mounted 480 volt 10 kva transformer mounted right next to a door opening such that when the door is opened the door hits the transformer. The door is for people to pass through. Is there a code violation here? Is there a code requirement that states a minimum distance between the transformer and the door opening?
TTBOMK, there is no code violation or transformer-to-door distance requirement.
 
Does the door open to clear the complete width of the door opening? If not there may be a building code issue.
 