Re: TRANSFORMER vs MOTOR
The KVA rating of a transformer (or a generator, for that matter) is based on the device?s ability to dissipate heat. For example, consider one set of loads that consists of 12 KW of real power and 5 KVAR of reactive power. Next, consider another set of loads that consists of 5 KW of real power and 12 KVAR of reactive power. In both cases, the total load adds up to 13 KVA. A transformer supplying the first set of loads would have to dissipate the same amount of heat as a transformer supplying the second set of loads. The first set has a power factor of 92%, and the second set has a power factor of 38%. But as Ed pointed out, the transformer is not going to care. All the transformer sees is the 13 KVA.
I believe that a motor is rated in HP or in order to allow the electrical designer to select motors to match the intended mechanical equipment. The pumps, fans, and compressors of the world are rated in HP or KW (or sometimes in BTU, but that can be converted to either HP or KW). In order to make the mechanical designers happy, we need to give them motors that have ratings at least as high as their mechanical equipment. But then we need to take one more step. In order to select the branch circuit conductors (and other stuff), we need to convert the motor HP to the actual current that the motor will draw. That requires us to take into account the motor?s electrical efficiency and its power factor. Fortunately, we don?t need to do the actual math. The NEC has tables that give us the amps, based on HP and voltage. The tables already take the efficiency and HP into account.