I have purchased and recently received an acme isolation transformer: 10 KVA 240x480 - 240/120. I was expecting some larger wires inside the xfmr. Primary side was 14ga and secondary was 12 ga! By my calculation I would get approximately 42 amps primary side (240v configuration) and 84 amps secondary side. Assuming 100% load on one phase, I was expecting something 4 ga or larger.
Are they using superconductors here? I plan to give a call to the manufacturer and discuss.
I have purchased and recently received an acme isolation transformer: 10 KVA 240x480 - 240/120. I was expecting some larger wires inside the xfmr. Primary side was 14ga and secondary was 12 ga! By my calculation I would get approximately 42 amps primary side (240v configuration) and 84 amps secondary side. Assuming 100% load on one phase, I was expecting something 4 ga or larger.
Are they using superconductors here? I plan to give a call to the manufacturer and discuss.