During an inspection the other day i had come across a 75 kva transformer in a room that has 24" of clearance in front of it. I wrote it up because of the requirements outlined in 110.26 (2014 NEC). The electrician came back and stated it did not need the clearance because it is not likely to require examination, servicing, etc. while energized. For a minute i was buying it but i do not see an exemption for transformers in this section of the code it just states "all electrical equipment". Am i in the wrong for requiring the 36" clearance?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
During an inspection the other day i had come across a 75 kva transformer in a room that has 24" of clearance in front of it. I wrote it up because of the requirements outlined in 110.26 (2014 NEC). The electrician came back and stated it did not need the clearance because it is not likely to require examination, servicing, etc. while energized. For a minute i was buying it but i do not see an exemption for transformers in this section of the code it just states "all electrical equipment". Am i in the wrong for requiring the 36" clearance?

I think you should reread what the code actually says. The "all equipment" reference is in 110.26 but does not provide for any specific requirements.

The specific requirements start in 110.26 (A) and refer to "equipment operating at 1000 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized".

I guess the key is whether transformers are likely to require examination, adjustment, servicing, or maintenance while energized.

Personally, I do not thing it is up to an inspector to make that kind of call.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
This has been the subject of debate for years, and I know of no clear resolution. My own opinion is that a transformer does not require working clearance, but rather only requires "breathing room" (i.e., 6" from any wall). The strongest argument I have heard against this opinion is that a transformer is likely to require thermographic "examination" (this is one of the terms used in 110.26), and that that process must be performed while the item is energized. My counter argument is that that process requires removal of a cover, but does not require reaching past the cover to the interior of the transformer. It is a visual inspection only. OK, it uses the "eyes" of the camera, not just human eyes, but the camera is looking into the enclosure from the outside. I don't believe this fits into the work description in 110.26.
 
Thanks for the input guys!! Reading it over a few more times and now getting feedback has opened my thinking up a little bit more I feel better about telling the electrician that i will accept the installation.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Thanks for the input guys!! Reading it over a few more times and now getting feedback has opened my thinking up a little bit more I feel better about telling the electrician that i will accept the installation.

it might be that whomever is the AHJ for your jurisdiction has some kind of ruling on this. You might want to take a look and find out before blessing it on your own.
 