Transformer Wye Secondary

Status
Not open for further replies.

curious23

Member
Location
Ohio
Occupation
Electrician
I have a 277/ 480 vac Wye supply feeding a 15kva, 480 delta primary to a 400 vac wye secondary. This transformer will supply a 400 vac 3 phase machine. My question is for the 400 vac wye secondary. When I bond the xo tap to ground, I will not need to run a neutral to the machine correct? I will run a equipment ground the machine for ground fault protection.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

Correct. The neutral need go no farther than the first secondary OCP/disconnect.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have a 277/ 480 vac Wye supply feeding a 15kva, 480 delta primary to a 400 vac wye secondary. This transformer will supply a 400 vac 3 phase machine. My question is for the 400 vac wye secondary. When I bond the xo tap to ground, I will not need to run a neutral to the machine correct? I will run a equipment ground the machine for ground fault protection.

Yes as Larry stated you would still install a SBJ from the X0 to make this a grounded system. You would also need a GEC.
Correct. The neutral need go no farther than the first secondary OCP/disconnect.
If the neutral is bonded within the transformer does it need to be brought out to the disconnect or would a SSBJ be all that's required?
 

Flicker Index

Senior Member
Location
Pac NW
Occupation
Lights
What is the machine? 400v suggests it's from Europe or Asia. If motor is the main piece, 480v/60Hz into a 400v/50Hz motor would be just the right voltage with the correct VHz ratio as if you're running at at 120% speed on a VFD... and that's exactly what's going to happen if it's a 50Hz equipment.

I can't tell you whether or not you run neutral to the machine. That depends on if the machine utilizes 230v between L-N (assuming it's 400Y/230 Euro/Asian equipment). Whether 1.2x RPM would be acceptable for proper operation is something you ought to do in consultation with the factory rep.
 