We have a 3 phase 480v step down to 208v transformer. There is no neutral required for the secondary load side. Does the X0 need to be bonded to structural steel if there is no need for a neutral?
250.32 is your code reference.
Separate buildings?:?
How about 250.20(B(1) instead?
One might be able to not ground the neutral - but only if it doesn't leave the transformer enclosure. You still have to ground something though, which leaves you with one of the phase conductors, or set up as an ungrounded system and provide ground fault monitoring.
If the neutral does leave the transformer then it definitely must be the conductor that gets grounded.
Most will read it that way, but I don't know it is worded quite the way it is intended. Do you see a problem other than possibly complying with this section with having a standby generator that is 480/277 to back up a corner grounded delta system and grounding a phase/leaving the neutral float on such system?I do not think the code section I cited allows an ungrounded 208Y/120V secondary.
99% of the time yes, you must bond that neutral. Some special situations one may not be using that neutral for anything, or even desiring to ground some other point of the source for a specific reason. You can't ground two points, that lets smoke out of insulation.kwired, my little brain cannot figure out all that.
Can we just keep it simple and bond XO to the steel?
It a wye secondary, life is much easier that way.
No muss or fuss.
for what its worth hood, yes, bond it but i always use a dedicated terminal block for equipments down low attached directly to the chassis, leaving the xo block with just one green bond jumper and a neutral..it also keeps that bare rebar conductor away from those ungrounded lugs... you know, when some one backs a fork lift into the tranny? oh, it happens... also is easy on the inspectors eyes B)
You do realize bonding at the first disconnecting means is also an option that is code compliant?Yes, I agree, the AHJ always looks at a transformer so when the X0 is bonded they smile! Thanks again guys!!!
EGC with primary yes, neutral only if the primary winding is going to utilize it. Delta primary winding doesn't utilize a neutral conductor.wouldnt that mean a neutral has to be pulled with the primarys? or lines..
we still want the separate der. neuty bonded, right?