What are some of the possible effects of running a 60Hz Transformer on 50Hz or vice versa?
What are some of the possible effects of running a 60Hz Transformer on 50Hz or vice versa?
Not much difference going 60Hz design on a 50Hz system, that's what the "50/60Hz" designs really are. But if it is designed strictly for a 50Hz system and given 60Hz, then it can saturate and run hot. That usually leads to an early demise.
Or, he was thinking of control power/machine tool transformers, where most the new generation <3kVA units are often dual rated for frequency.i suspect Jraef just didnt have his 2nd beer yet, and was thinking of a heavy customer problem when he wrote that.