Hello all, if this question should be in a non- solar forum just let me know...
I want to make certain my math is right on sizing and overcurrent protection so bare with me here. My NEC book is in my work truck 150 miles away making it a bit harder.
I'm installing a 142.1kW solar system on a building. Using (5) 3 phase 277/ 480V inverters totalling 240A (with 1.25 OC protection included)
The grid voltage is 120/ 208V and I'll be using a step up transformer to the 277/ 480V.
This is my math 240*480*1.732 = 199,526/ 1,000 = 199.5 So I'm planning on using a 225kVA transformer, which is the next standard size up... Am I all good so far?
Then for determining the primary amps I'm not sure if I should use the 199.5 or the 225kVA in my math... So coming up with the following
199.5*1,000 = 199,500 208*1.732 = 360 199,500/360 = 554A Rounded up to 600A fuse size
OR
225*1,000 = 225,000 208*1.732 = 360 225,000/360 = 625A Rounded up[ to 650A
OR am I just totally wrong on both??? They both sound kinda high to me compared to a similar one I just installed.
I'm trying to help the designer meet a deadline with plans and I will be installing all major components.
I want to make certain my math is right on sizing and overcurrent protection so bare with me here. My NEC book is in my work truck 150 miles away making it a bit harder.
I'm installing a 142.1kW solar system on a building. Using (5) 3 phase 277/ 480V inverters totalling 240A (with 1.25 OC protection included)
The grid voltage is 120/ 208V and I'll be using a step up transformer to the 277/ 480V.
This is my math 240*480*1.732 = 199,526/ 1,000 = 199.5 So I'm planning on using a 225kVA transformer, which is the next standard size up... Am I all good so far?
Then for determining the primary amps I'm not sure if I should use the 199.5 or the 225kVA in my math... So coming up with the following
199.5*1,000 = 199,500 208*1.732 = 360 199,500/360 = 554A Rounded up to 600A fuse size
OR
225*1,000 = 225,000 208*1.732 = 360 225,000/360 = 625A Rounded up[ to 650A
OR am I just totally wrong on both??? They both sound kinda high to me compared to a similar one I just installed.
I'm trying to help the designer meet a deadline with plans and I will be installing all major components.