codequestion

Banned
Location
MD, USA
I have 75kva three phase 480/277v to 120/208v transformer. The secondary transformer feeder is 145 feet long and terminates at panel with 200 amps main breaker. The primary has 100 amp fused disco in same room. Does the secondary require breaker due to feeder being 145 feet per code 245.21 or other article?

Sent from my SM-G935U using Tapatalk
 
Last edited:
Yes, unless the secondary conductors are outside, they need overcurrent protection per one of the rules in 240.21(C).
 
Even though their is main breaker in the panel secondary? Also their is no over 25 feet 240.21 (C). My length is 145 feet.

Sent from my SM-G935U using Tapatalk
Correct, maximum secondary length before first overcurrent device is 25 feet, unless it is outdoors.
 
Correct, maximum secondary length before first overcurrent device is 25 feet, unless it is outdoors.
So I would need total of 5 overcurrent devices one very 25 feet or just one 25 feet and I am good? Also their is 10 feet as well 240.21 (C). So how does that work?

Sent from my SM-G935U using Tapatalk
 
So I would need total of 5 overcurrent devices one very 25 feet or just one 25 feet and I am good? Also their is 10 feet as well 240.21 (C). So how does that work?

Sent from my SM-G935U using Tapatalk
Actually unless this is an industrial installation where conditions of maintenance and supervision ensure that only qualified persons service the systems - the 10 foot rule is what applies, and no you don't need an overcurrent device every 25 feet, once you hit the first device you no longer have feeder tap or secondary conductors you have a "feeder" beyond that point.
 
Actually unless this is an industrial installation where conditions of maintenance and supervision ensure that only qualified persons service the systems - the 10 foot rule is what applies, and no you don't need an overcurrent device every 25 feet, once you hit the first device you no longer have feeder tap or secondary conductors you have a "feeder" beyond that point.
What about 240.21 (c)(6)? Is it for 25 feet rule for non industrial location? I am still confuse so I can either apply 10 feet or 25 feet rule?

Sent from my SM-G935U using Tapatalk
 
What about 240.21 (c)(6)? Is it for 25 feet rule for non industrial location? I am still confuse so I can either apply 10 feet or 25 feet rule?

Sent from my SM-G935U using Tapatalk


See 240.21(C)(2), 10 foot transformer secondary tap rule -
240.21(C)(2)(4):
  • Find the ratio between primary and secondary voltages, i.e. 480/208 = 2.31
  • Find the rating of the primary side overcurrent device...Primary Rating = 75kVA/480 x 1.732 = 90 x 1.25%=112.7 - round up to next std size = 125A - ref Art 240.6.
  • Divide rating of 125A by 10 = 12.5.
Minimum allowable conductor would be, 2.31 x 12.5 = 28.875 =29A, which equals min #10 Awg for secondary side. The caveat is the conductors cannot be less than the loads supplied by the secondary, see 240.21(C)(2)(1). This is why the 10ft tap rule is seldom used.
 
Last edited:
What about 240.21 (c)(6)? Is it for 25 feet rule for non industrial location? I am still confuse so I can either apply 10 feet or 25 feet rule?

Sent from my SM-G935U using Tapatalk
Yes, thought something wasn't quite right when I posted before because I was pretty sure you could go up to 25 feet in any location - must meet all the conditions mentioned though.
 
See 240.21(C)(2), 10 foot transformer secondary tap rule -
240.21(C)(2)(4):
  • Find the ratio between primary and secondary voltages, i.e. 480/208 = 2.31
  • Find the rating of the primary side overcurrent device...Primary Rating = 75kVA/480 x 1.732 = 90 x 1.25%=112.7 - round up to next std size = 125A - ref Art 240.6.
  • Divide rating of 125A by 10 = 12.5.
Minimum allowable conductor would be, 2.31 x 12.5 = 28.875 =29A, which equals min #10 Awg for secondary side. The caveat is the conductors cannot be less than the loads supplied by the secondary, see 240.21(C)(2)(1). This is why the 10ft tap rule is seldom used.
10 foot tap rule is used a lot. In your example above you have a transformer secondary rating of 208 amps. If you are supplying a 200 amp overcurrent device you will have 200 amp conductor - which is well above the minimum needed 29 amps. The limitation of that section mostly only effects you if you were supplying say an individual 15 amp breaker from said transformer - it would need to be supplied with 10AWG conductor even though the load is 15 or less. Load side of the breaker could then be 14 AWG.
 
10 foot tap rule is used a lot. In your example above you have a transformer secondary rating of 208 amps. If you are supplying a 200 amp overcurrent device you will have 200 amp conductor - which is well above the minimum needed 29 amps. The limitation of that section mostly only effects you if you were supplying say an individual 15 amp breaker from said transformer - it would need to be supplied with 10AWG conductor even though the load is 15 or less. Load side of the breaker could then be 14 AWG.

You could incorporate both the 10 and 25 foot tap rules from the same xfmr
secondary - using my example of minimum 29A for a very lightly loaded panel along with your example of a 200A. The key factor is sizing the conductors to the load as I stated above - ref 240.21(C)(2)(1).
In petro-chem we rarely use the 10 foot rule. In fact we don’t see the 25 ft tap rule often either since most of our transformers are located outdoors to begin with.


Sent from my iPhone using Tapatalk
 
You could incorporate both the 10 and 25 foot tap rules from the same xfmr
secondary - using my example of minimum 29A for a very lightly loaded panel along with your example of a 200A. The key factor is sizing the conductors to the load as I stated above - ref 240.21(C)(2)(1).
In petro-chem we rarely use the 10 foot rule. In fact we don’t see the 25 ft tap rule often either since most of our transformers are located outdoors to begin with.


Sent from my iPhone using Tapatalk
Yes, but for OP's transformer there is only an issue with a tapped load of under 29 amps when using the 10 foot rule, in such case the supply side of your overcurrent device needs to be at least 10 AWG instead of 14 AWG. Anything over 29 amps requires conductor sized at least to the load anyway.

25 foot rule is where you would need larger conductor. With 125 amp primary device and a 2.31 voltage ratio you would need a 96 amp conductor minimum for 25 foot rule, even if only supplying a 15 amp breaker.
 
Yes, but for OP's transformer there is only an issue with a tapped load of under 29 amps when using the 10 foot rule, in such case the supply side of your overcurrent device needs to be at least 10 AWG instead of 14 AWG. Anything over 29 amps requires conductor sized at least to the load anyway.

25 foot rule is where you would need larger conductor. With 125 amp primary device and a 2.31 voltage ratio you would need a 96 amp conductor minimum for 25 foot rule, even if only supplying a 15 amp breaker.


I agree. I was only giving a general example of the 10 foot tap rule since the OP had expressed some level of confusion. There are actually three transformer 25 foot tap rules: 240.21(C)(2), 240.21(C)(6) and 240.21(B)(3) - this last one gets overlooked quite a bit since it involves both primary and secondary conductors.
 
Last edited:
Additional info to post #1: secondary side panelboard is going to be located in tenant space not relocatable and the transformer is in electrical room. Its 145 feet of secondary cables between the transformer and the secondary panelboard sized 3/0 awg.

The secondary side panelboard calculated demand load is 191 amps, panelboard bus 200 amps, panelboard main circuit breaker 200 amps.

1. If I use ten feet rule 240.21 (C)(2):

-240.21 (2)(1)(a)(b): i am using 3/0 awg secondary conductors amapcity at 75C 200 amps.

-240.21 (2)(2): they dont extend beyond secondary panelboard but thats more than 10 feet away. So not sure how this applies unless i provide 200 amp enclosed circuit breaker less than 10 feet transformer secondary.

-240.21 (2)(3): that applies but i am guessing they are talking about less than 10 feet. Panelboard is 145 feet away. Not sure how this applies unless provide 200 amp enclosed circuit breaker less than 10 feet.

-240 21 (2)(4): Primary overcurrent protrctive device I have is 100 amps. Ampacity of secondary conductor is 200 amps. ( 200 x10) which is less than 100x (480/208). I guess okay.

2. If i use 25 foot rule 240.21(C)(6):

- 240.21 (C)(6)(1): 3/0 awg secondary cable ampacity 200 amp is greater than (480/208)*(100/3).

-240.21(C)(6)(2): Have to provide 200 amps enclosed circuit breaker less than 25 feet from transformer secondary. However from 15 feet from transformer secondary the cables would go to other rooms.

-240.21 (C)(6)(3): That applies to secondary conductors less than 25 feet. I have secondary condcutors 145 feet. So the install up to 25 feet would have to comply and not the rest?

3. 240.21(C) says condctors connected to transformer without overcurrent protection at the secondary as specified in 240.21 (C)(1) to (C)(6). C1 does not apply to post #1 i guess. C2 to C6 are either 10feet or 25 deet rules but I have 145 feet. So C1 to C6 does not apply in my case so I have to provide with overcurrent protection just where??


I guess I could be interpretting #1 to #3 above wrong.

Sent from my SM-G935U using Tapatalk
 
Last edited:
Additional info to post #1: secondary side panelboard is going to be located in tenant space not relocatable and the transformer is in electrical room. Its 145 feet of secondary cables between the transformer and the secondary panelboard sized 3/0 awg.

The secondary side panelboard calculated demand load is 191 amps, panelboard bus 200 amps, panelboard main circuit breaker 200 amps.

1. If I use ten feet rule 240.21 (C)(2):

-240.21 (2)(1)(a)(b): i am using 3/0 awg secondary conductors amapcity at 75C 200 amps.

-240.21 (2)(2): they dont extend beyond secondary panelboard but thats more than 10 feet away. Can't apply 10 foot rule then, simple as that. So not sure how this applies unless i provide 200 amp enclosed circuit breaker less than 10 feet transformer secondary.

-240.21 (2)(3): that applies but i am guessing they are talking about less than 10 feet. Panelboard is 145 feet away. Not sure how this applies unless provide 200 amp enclosed circuit breaker less than 10 feet.

-240 21 (2)(4): Primary overcurrent protrctive device I have is 100 amps. Ampacity of secondary conductor is 200 amps. ( 200 x10) which is less than 100x (480/208). I guess okay.

2. If i use 25 foot rule 240.21(C)(6):

- 240.21 (C)(6)(1): 3/0 awg secondary cable ampacity 200 amp is greater than (480/208)*(100/3).

-240.21(C)(6)(2): Have to provide 200 amps enclosed circuit breaker less than 25 feet from transformer secondary. However from 15 feet from transformer secondary the cables would go to other rooms.

-240.21 (C)(6)(3): That applies to secondary conductors less than 25 feet. I have secondary condcutors 145 feet. Again can't apply 25 foot rule because you are over 25 feet. So the install up to 25 feet would have to comply and not the rest?

3. 240.21(C) says condctors connected to transformer without overcurrent protection at the secondary as specified in 240.21 (C)(1) to (C)(6). C1 does not apply to post #1 i guess. C2 to C6 are either 10feet or 25 deet rules but I have 145 feet. So C1 to C6 does not apply in my case so I have to provide with overcurrent protection just where??


I guess I could be interpretting #1 to #3 above wrong.

Sent from my SM-G935U using Tapatalk
You need to apply overcurrent protection within 10 feet or 25 feet and at same time comply with provisions that go with which ever rule you are applying. Once you have a place for the overcurrent protection - the rest of the downstream conductors are no longer feeder taps or transformer secondary conductors that must comply with 240.21, they are simply feeders or branch circuits.
 