hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 30kva transformer primary of 208V going to 480V feeding light poles. The transformer secondary within 25 feet has fused disconnect sized for 20A fuse. The load of light poles is 3 kva so 20A fuse is ok. However 20A fuse on 30kva 208v to 480v can it be sized way less than transformer fla nec 2014 Article 450?