Greg Wrenn
Member
I am in the process of moving drills between two plants. The plant one has a 480 Delta system with a 240 volt bus bar system that the drills started at. I am transferring them to plant two which has a 480 Wye system with the bus bar running 480 volts. I told the manufacturer that I needed transformers that would step down to a 240 Wye system so that I could have a neutral. They sent me, I believe, a 240 delta because their is no "xo" to hook up a neutral. So I am assuming their is no way to hook up a 120 receptacle to this because their is no neutral. First, is this accurate? and second what transformer to I need to ask for to get this accomplished I have some 240 volt drills that run 120 volt pumps. We are transferring these machines from a plant that had a 240 delta bus bar system to a plant that has a 480 wye bus bar system.
In another thread someone mentioned what do I mean by 240 volt drills running 120 volt pumps. These drills had receptacles tied in to the 240 volt disconnect box at the machine but only tied in to one leg so that their would be 120 volts to run the pumps. Unless I am missing something I can not do this with the transformers that I was sent.
In another thread someone mentioned what do I mean by 240 volt drills running 120 volt pumps. These drills had receptacles tied in to the 240 volt disconnect box at the machine but only tied in to one leg so that their would be 120 volts to run the pumps. Unless I am missing something I can not do this with the transformers that I was sent.