Transformer

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Would most transformer instruction delta to wye 15kva and above dry type indicate which point to connect to neutral secondary side?Does anyone know that have installed transformer
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Yes, there should be instructions, and also a diagram label on the unit.

There should be a terminal marked X-0; that's the secondary neutral.

Maybe I'm confused about your question; this is pretty basic stuff.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There are variations as to having a 120v (only) secondary or a 240/120 and different manufactures might label terminals or conductors differently. As Larry suggests, research the specific transformer.
For general info you can Google 240/120 transformer connections and view several diagrams.
 