Transformer

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have seconder conductors for transformer 3#3 awg,1#3/0 awg N and was wonder would the supply side bonding jumper table 250.102(C)(1) be sized per #3 or #3/0awg?
 
I have seconder conductors for transformer 3#3 awg,1#3/0 awg N and was wonder would the supply side bonding jumper table 250.102(C)(1) be sized per #3 or #3/0awg?
Table 250.102(C)(1) provides the answer to your question, right in the table itself.
 
How did you do taking tests on your own?

This is not a test. None of my posts are test questions