I have seconder conductors for transformer 3#3 awg,1#3/0 awg N and was wonder would the supply side bonding jumper table 250.102(C)(1) be sized per #3 or #3/0awg?
Table 250.102(C)(1) provides the answer to your question, right in the table itself.I have seconder conductors for transformer 3#3 awg,1#3/0 awg N and was wonder would the supply side bonding jumper table 250.102(C)(1) be sized per #3 or #3/0awg?
Table 250.102(C)(1) provides the answer to your question, right in the table itself.
How did you do taking tests on your own?
I understand that. That wasn't the point I was trying to make.This is not a test. None of my posts are test questions
Ungrounded conductor? So thats #3 not #3/0awg?