Transformer

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have seconder conductors for transformer 3#3 awg,1#3/0 awg N and was wonder would the supply side bonding jumper table 250.102(C)(1) be sized per #3 or #3/0awg?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I have seconder conductors for transformer 3#3 awg,1#3/0 awg N and was wonder would the supply side bonding jumper table 250.102(C)(1) be sized per #3 or #3/0awg?
Table 250.102(C)(1) provides the answer to your question, right in the table itself.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
How did you do taking tests on your own?

This is not a test. None of my posts are test questions


6de8a7c226e40fb4668f5f4dc7f7678f.jpg
 