cf,
Definitely subject to senior moments.
My point, based on POCO in this area, is that they don't corner ground any of their delta services. If you request and they agree to supply a delta 3 wire supply, then you can elect to corner ground or leave it ungrounded at your service equipment.
OP stated POCO supplied him with a corner grounded system. May be true, but would not happen with any of the POCOs in my inspection area.
I agree, of course, if POCO grounds anything, that's what you get.
I mentioned the transformer as, in all probabilty, he will need 120 volt power for something, and 210.6(D) would seem to prohibit most 480v lighting.
As I recall, this started with the OP trying to obtain 277v and as of yet, he might not need to
eds, If the system is already corner grounded prior to it's reaching your service, that's what you will have to live with. The 3 phase motors care less (grounded or ungrounded) as long as they receive their rated voltage.