Are you guys bonding the DC equipment ground to Earth with the Transformerless inverter?

Sent from my SAMSUNG-SM-G900A using Tapatalk

This already happens, when you bond the AC equipment ground to the premises's EGC system that is bonded to Earth at the service electrode.

The DC and AC equipment ground terminations are internally bonded directly inside the TL inverters.
 