I was recently doing some transformer calculation refresher material, and it was mentioned that by nature transformers are current limiting. Also it was mentioned that this could possibly make OVCP slightly less important.
I seen transformer secondary short circuit formulas and to me it seemed like the current could be 50 times more than the transformers rating. I guess it is technically limiting but it can still have extremely high currents.
For example if I put a 200amp load on a transformer secondary rated at 100amps with no protection would the current somehow be limited by transformer impedance to 100amps?
I had little luck on web searches
I seen transformer secondary short circuit formulas and to me it seemed like the current could be 50 times more than the transformers rating. I guess it is technically limiting but it can still have extremely high currents.
For example if I put a 200amp load on a transformer secondary rated at 100amps with no protection would the current somehow be limited by transformer impedance to 100amps?