M Mainstreet New member Nov 16, 2007 #1 I put in a 480v single phase to 120v 5kva transformer to get a couple of outdoor outlets going but the GFCI's will not work at all. I am getting 120v on secondary side and the lights are on. What am I missing?
I put in a 480v single phase to 120v 5kva transformer to get a couple of outdoor outlets going but the GFCI's will not work at all. I am getting 120v on secondary side and the lights are on. What am I missing?
R rlMutch Senior Member Location WA state Nov 16, 2007 #2 How did you ground the secondary (120V side) of the transformer?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 17, 2007 #3 How did you try to test the GFCIs? Don