- Massachusetts
For a while I have been assigned to a factory, they are getting two new identical machines and I have been told to wire them.
Here is what I have.
The machines are in route from Italy, I have some info.
In the paperwork it states "100 amp 400 volt 3 phase 4 wire supply".
On the phone I was told 30 KW max 10 KW normally. (A far cry from 100 amps)
It was decided by management to use a 480-400Y/231 volt transformer for each machine and they had the purchasing dept get them.
They got two 93 KVA 480-400Y/231 volt transformers (A Bit large for the load)
Management also decided I would get one three pole space in an existing panelboard and I am to re-use an existing 2" EMT.
In a nut shell;
One Feeder that can fit in a 2" EMT.
Two 93 KVA 480-400Y/231 volt transformers.
Two machines that apparently draw 14 to 43 amps but are labeled as a 100 amps.
I already know what I have planed and 70% of it is done.
I am interested how you others would have handled this,
Conductor sizes?
OCPDs?
I am sure there are 100 different ways it could be done, I am hoping my way was one of them.:grin:
In a nut shell;
Conductor sizes?
OCPDs?