Transformers-Copper / Aluminum?

Status
Not open for further replies.

zooby

Senior Member
Location
Indiana
Occupation
maint. electrician
looking at replacing a 30kva 480 to 120-208 transformer. Are there any comments about alum windings ? My first thought is to stay with copper but times as they are...... Thanks---Doug
 
I wound transformers for welders and battery chargers for about 15 months.
The primaries were usually copper and the secondaries aluminum.
Depends on what your EE/designer specs. No problem.

Ron
 
I would not (and did not) hesitate to use aluminum windings in a transformer.

I would also expect that they'd be the norm in a transformer that size (step down 30kva).
 
looking at replacing a 30kva 480 to 120-208 transformer. Are there any comments about alum windings ? My first thought is to stay with copper but times as they are...... Thanks---Doug
Is the space tight around the transformer? I'd expect it to be a little larger with aluminum windings instead of copper.
 
looking at replacing a 30kva 480 to 120-208 transformer. Are there any comments about alum windings ? My first thought is to stay with copper but times as they are...... Thanks---Doug
In sizes less than 150kVA aluminum windings have been the standard warehouse construction, from manufacturers like Square D and GE for some 40 years or more
 
In sizes less than 150kVA aluminum windings have been the standard warehouse construction, from manufacturers like Square D and GE for some 40 years or more
Totally agree. And also, just checked a Hammond catalog I have on my laptop, their case sizes for copper vs. alum transformers are identical until you get to 225 kva. So no real difference in physical size for such small transformers.

Obviously, the al is a little lighter than copper, but at small sizes like a 30 kva, it's only a ~30 lb difference.

Reading the first post, the OP sort of suggests there is a copper transformer in place right now. Are you sure?
 
Is the space tight around the transformer? I'd expect it to be a little larger with aluminum windings instead of copper.
No but it does sit on a small concrete pad. I will check the dimensions of that today. Thanks!
 
Totally agree. And also, just checked a Hammond catalog I have on my laptop, their case sizes for copper vs. alum transformers are identical until you get to 225 kva. So no real difference in physical size for such small transformers.

Obviously, the al is a little lighter than copper, but at small sizes like a 30 kva, it's only a ~30 lb difference.

Reading the first post, the OP sort of suggests there is a copper transformer in place right now. Are you sure?

smaller WRG (2).jpgHere is the pic. Thanks you!
 
The CU at the end of the part number very likely indicates that it has copper windings.
If the transformer has failed, it may be more likely it was an insulation failure given the 150 deg C remperature rise. Appropriate insulation materials are used for the temperature rise of the design, but higher temperatures still will tend to increase failure rates.

If continuity testing shows that there are no open windings, then if the transformer failed its likely due to the insulation and not the conductors.
 