Is the space tight around the transformer? I'd expect it to be a little larger with aluminum windings instead of copper.looking at replacing a 30kva 480 to 120-208 transformer. Are there any comments about alum windings ? My first thought is to stay with copper but times as they are...... Thanks---Doug
In sizes less than 150kVA aluminum windings have been the standard warehouse construction, from manufacturers like Square D and GE for some 40 years or morelooking at replacing a 30kva 480 to 120-208 transformer. Are there any comments about alum windings ? My first thought is to stay with copper but times as they are...... Thanks---Doug
Totally agree. And also, just checked a Hammond catalog I have on my laptop, their case sizes for copper vs. alum transformers are identical until you get to 225 kva. So no real difference in physical size for such small transformers.In sizes less than 150kVA aluminum windings have been the standard warehouse construction, from manufacturers like Square D and GE for some 40 years or more
No but it does sit on a small concrete pad. I will check the dimensions of that today. Thanks!Is the space tight around the transformer? I'd expect it to be a little larger with aluminum windings instead of copper.
Totally agree. And also, just checked a Hammond catalog I have on my laptop, their case sizes for copper vs. alum transformers are identical until you get to 225 kva. So no real difference in physical size for such small transformers.
Obviously, the al is a little lighter than copper, but at small sizes like a 30 kva, it's only a ~30 lb difference.
Reading the first post, the OP sort of suggests there is a copper transformer in place right now. Are you sure?