Hello all,
This might be silly but I am so used to in my head going one way in the usual power distribution that now when I am presented the reverse power flow, its making do a double take.
Typically, we have a service and we envision that to be a Delta to wye. Three phase 4 wire. Any unbalanced current returns on the neutral back to the XO in the transformer. We have a MBJ at the service location and that bond occurs only at that one point (rest are SBJs).
I have a situation where I have a service that is 208V120V 3ph 4 wire. The service/meter / main disconnect switch is about 400ft away as the crow flies from a step up transformer. The transformer is a 3ph customer owned step up transformer, however, it is wired Y to Delta. Y being the 208/120V. There is a N-G in there (I didn't get to see inside the main switch). On the secondary which is the high side is 480V (not 480V/277V, its a delta and no neutral).
Only 3 phases and an EGC is sent from that transformer (no neutral). That feed is ran about 800ft until it hits the building it is servicing. The building has a main disconnect.
That building has a generator and a transfer switch. (The generator has a neutral and it is terminated in the transfer switch but the neutral lug is isolated from everything and since the main service does not have a neutral, there is no intermixing of neutrals there).
I assume that I drive my ground electrodes at the building and just terminate to the main switches ground lug, nothing more?
There are unbalanced Phase to Phase loads on the 480V system. We do see a unbalanced voltages. I assume its from the unbalance? What other concerns are there with running an unbalanced delta as your feed to your loads? The largest loads are 3 ph motors, but they are on seldom. Majority of the time its an odd number of 1 ph heaters.
This might be silly but I am so used to in my head going one way in the usual power distribution that now when I am presented the reverse power flow, its making do a double take.
Typically, we have a service and we envision that to be a Delta to wye. Three phase 4 wire. Any unbalanced current returns on the neutral back to the XO in the transformer. We have a MBJ at the service location and that bond occurs only at that one point (rest are SBJs).
I have a situation where I have a service that is 208V120V 3ph 4 wire. The service/meter / main disconnect switch is about 400ft away as the crow flies from a step up transformer. The transformer is a 3ph customer owned step up transformer, however, it is wired Y to Delta. Y being the 208/120V. There is a N-G in there (I didn't get to see inside the main switch). On the secondary which is the high side is 480V (not 480V/277V, its a delta and no neutral).
Only 3 phases and an EGC is sent from that transformer (no neutral). That feed is ran about 800ft until it hits the building it is servicing. The building has a main disconnect.
That building has a generator and a transfer switch. (The generator has a neutral and it is terminated in the transfer switch but the neutral lug is isolated from everything and since the main service does not have a neutral, there is no intermixing of neutrals there).
I assume that I drive my ground electrodes at the building and just terminate to the main switches ground lug, nothing more?
There are unbalanced Phase to Phase loads on the 480V system. We do see a unbalanced voltages. I assume its from the unbalance? What other concerns are there with running an unbalanced delta as your feed to your loads? The largest loads are 3 ph motors, but they are on seldom. Majority of the time its an odd number of 1 ph heaters.