Re: Transformers on dairy farms
Unbalanced secondary loads will cause primary neutral currents to flow in the ground back to the substation source unless the transformer has a delta winding.
Example: assume a 200A, single phase 277V load on A phase. 7.7 amps will flow in the A phase primary winding. (200 x 277/7200 = 7.7 amps). Assume no load on B or C phase. That means there can be no current in the primary B&C windings. The only place the 7.7 amps in the A phase winding can go is out the neutral and into the ground. That current has to travel in the ground back to the utility substation transformer's grounded neutral.
Any unbalanced neutral currents, including harmonics, will cause ground currents in the primary neutral "circuit" that is the ground.
Usually Y-Y Xfmrs are padmount type, fed with shielded cable or URD cable. The grounded cable shields provide a ground return path for the unbalanced currents.
The Y-Y's might be a source of the stray voltages but I would eliminate other possible causes first: improper neutral groundng, poor gorunds, etc.
edit:
Just saw that you said it was fed by delta system. If any phase imbalance occurs, I don't see how the unbalance current can get back to the ungrounded delta winding.
[ June 08, 2005, 09:06 PM: Message edited by: rcwilson ]