augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Sep 17, 2020 #1 Anyone have input on providing a grounding electrode system for a transformer located on a floating dock ?
Anyone have input on providing a grounding electrode system for a transformer located on a floating dock ?
Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician Sep 17, 2020 #2 Use floating ground rods!
Greentagger Senior Member Location Texas Occupation Master Electrician, Electrical Inspector Sep 17, 2020 #3 553.4. Location of service equipment not permitted on the floating structure? Sorry not familiar with that installation.