In this type of arrangement, the 13.8 kV breakers provide power to a group of transformers, but the transformers all have individual primary fusing in accordance with 450.3(A). If your arrangement is typical of a double-ended campus-type distribution system, the A & B sides are brought into each transformer disconnect switch, such that if either side is lost, you can select the alternate feeder. So each side could power all of the transformers in a given group.
The issue then becomes selection of an instantaneous settings that will tolerate the inrush of the group, which in theory is 8-12X. I've tried to find data on that cumulative effect, to no avail. We will be doing measurements in the next few weeks to get at a good number, where we'll energize a group of 8-10, 13.8 kV transformers ranging in size from 75-500 kVA, for a total of about 1500 kVA. I'll use that instantaneous measurement to establish a limit as to how much I can energize at once in a given group of transformers.
Power systems are always constrained by the Utility overcurrent protective device (ocpd), which ultimately determines how much cumulative KVA can be switched on at once. Ideally you'd like to bring the system up with as little sectionalizing as possible, but you must stay within the limits of the Utility ocpd.
The other consideration is conductor overcurrent protection, where 240.100 allows you to exceed the ampacity of the conductors, with conductor service calculations essentially being the overload protection.
John M