Hey all, I know that this topic has probably been discussed here on this forum hundreds of times, but I need some clarification on a few things. Regardless of how much reading and "googling" that I do on this subject, there are still some items that are confusing to me. As I state in my thread title, I have read/continue to read Articles 450 and 240 to try and fully understand this subject.
Here is my specific situation on a Data Center project in Newark, NJ. I have a 480V, 600A Distribution Panelboard that is feeding a 75 KVA transformer, from a 125A/3P circuit breaker. The DP will be located in a newly constructed satellite electric closet, and the 75 KVA transformer will be located in the adjacent room, the 3rd Floor Main Electric Room. The lateral distance from the DP to the transformer is approximately 14', and the distance of the primary feeder counting "ups & downs" is approximately 20'. I have my primary side feeder to the 75 KVA transformer set at 3#2 & 1#6G. in 1 1/4"C.
Question #1: Since the DP is in the other room, is extra protection required before the primary feeder hits the primary side of the transformer? I am thinking that it is not required, but I just want to make sure, because I need all necessary scope accounted for.
The low voltage panelboard that the 75 KVA transformer is feeding is a 208/120V, 225A MLO panelboard, and is located right next to the 480V DP in the satellite electric closet. The lateral distance from the transformer to the LV panel is approximately 17', and the distance of the secondary feeder counting "ups & downs" is approximately 22', thus within 25'. I have my secondary side feeder to the 225A panelboard set at 4#250 KCMIL & 1#2G. in 2 1/2"C.
Question #2: Since the LV panelboard is in the other room, is extra protection (i.e. either a 225A enclosed circuit breaker or a 400A disconnect switch fused @ 225A) required for the feeder after coming out of the secondary side of the transformer, before connecting to the LV panelboard? As in Question #1, I am thinking that it is not required because the feeder run is less than 25', but again I just want to be sure.
I would greatly appreciate all responses and guidance that you can give me for this design example and topic in general. Thanks very much and look forward to your responses!
Regards,
Anthony Giordano
Here is my specific situation on a Data Center project in Newark, NJ. I have a 480V, 600A Distribution Panelboard that is feeding a 75 KVA transformer, from a 125A/3P circuit breaker. The DP will be located in a newly constructed satellite electric closet, and the 75 KVA transformer will be located in the adjacent room, the 3rd Floor Main Electric Room. The lateral distance from the DP to the transformer is approximately 14', and the distance of the primary feeder counting "ups & downs" is approximately 20'. I have my primary side feeder to the 75 KVA transformer set at 3#2 & 1#6G. in 1 1/4"C.
Question #1: Since the DP is in the other room, is extra protection required before the primary feeder hits the primary side of the transformer? I am thinking that it is not required, but I just want to make sure, because I need all necessary scope accounted for.
The low voltage panelboard that the 75 KVA transformer is feeding is a 208/120V, 225A MLO panelboard, and is located right next to the 480V DP in the satellite electric closet. The lateral distance from the transformer to the LV panel is approximately 17', and the distance of the secondary feeder counting "ups & downs" is approximately 22', thus within 25'. I have my secondary side feeder to the 225A panelboard set at 4#250 KCMIL & 1#2G. in 2 1/2"C.
Question #2: Since the LV panelboard is in the other room, is extra protection (i.e. either a 225A enclosed circuit breaker or a 400A disconnect switch fused @ 225A) required for the feeder after coming out of the secondary side of the transformer, before connecting to the LV panelboard? As in Question #1, I am thinking that it is not required because the feeder run is less than 25', but again I just want to be sure.
I would greatly appreciate all responses and guidance that you can give me for this design example and topic in general. Thanks very much and look forward to your responses!
Regards,
Anthony Giordano